TimB100000
Member
- Location
- California
- Occupation
- Contractor
I've spent the evening looking at a few hundred posts on low-voltage pool light grounding (not bonding), and can't seem to find a satisfactory answer to this, even though the topic of pool lights has been covered extensively. I'm looking at a 12V pool light, and the cable from the lumiere includes a green ground wire. The light will be connected to a isolated-secondary transformer (Intermatic PX300) via PVC conduit. The transformer has an "Equipment Ground" lug, which is the transformer housing (mains ground.) I could connect the ground wire of the lumiere to the equipment grounding lug of the transformer, but that doesn't make any sense to me. Since there's no potential between either leg of an isolated secondary and mains ground, even if there was a dead short between one of the secondary wires to the metal housing of the fixture, no current is going to flow to mains ground. Perhaps if the transformer isolation failed, and mains current was flowing in one of the secondary wires, AND the lumiere allowed the secondary to short to the housing, a ground would help. But that risk seems lower than the risk that if there's a short to ground anywhere in my house, some amount of current will find its way into the pool area through that ground wire. If the resistance to ground through that path isn't much higher than resistance to ground via the panel, that current could be significant. Or if the pump ground became disconnected, that lumiere ground path might become the pump's ground path, which it was never intended to be. If I've got an isolated secondary, why would I want to introduce a mains-referenced ground? Am I missing something?
Tim
Tim