The ground wire from a service switchboard to the main building ground bar is an equipment grounding conductor, correct?
The ground wire from a service switchboard to the main building ground bar is an equipment grounding conductor, correct?
The ground wire from a service switchboard to the main building ground bar is an equipment grounding conductor, correct?
More details on what this "main building ground bar" is critical to the answer.The ground wire from a service switchboard to the main building ground bar is an equipment grounding conductor, correct?
250.30(A)(6) calls it a grounding electrode conductor tap.If it is a place for multiple services to tie together and then connect the grounding electrode system to it - each connection to each service is a bonding jumper I would think.
Ok thanks. I was aware of what that section allows, but did not look to see if they gave a name to such a conductor. Sort of a name that only applies to that section and not a name that applies to the NEC in general or even art 250 in general - or it would probably be in art 100 or 250.2.250.30(A)(6) calls it a grounding electrode conductor tap.
The ground wire from a service switchboard to the main building ground bar is an equipment grounding conductor, correct?
The ground wire from a service switchboard to the main building ground bar is an equipment grounding conductor, correct?
The building ground bar is an extension of the grounding electrode system therefore an external grounding conductor form the switchboard is most likely the GEC.
only if it is.
it could also just be a place to land EGCs.
the term is ambiguous.
Building grounding bars are either bolted or welded to building steel - this is an extension of grounding electrode system or equipotential grid.