EGC Question

Status
Not open for further replies.

Steve-Ty

Member
Location
New jersey
Occupation
Electrical Engineer/Electrician
A FEEDER CONTAINS SIX ALUMINUM CONDUCTORS INSTALLED IN A PVC CONDUIT. TWO CONDUCTORS PER PHASE ARE PROTECTED BY A 400 AMP FUSE. WHAT SIZE ALUMINUM EQUIPMENT GROUNDING CONDUCTOR IS REQUIRED?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Look at Table 250.122 for 400 amps.

Welcome to the Forum and please turn off the Caps lock. :)
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
After you check 250.122 ... what size are the phase conductors ?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
As per 250.122, size of an equipment grounding conductor for a 400 amp circuit is #1 Aluminum.
But the size of your phase conductors (unknown) may affect that.
250.122(B) might require an larger EGC if you phase conductors are oversized.
 
  • Like
Reactions: ron

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
But the size of your phase conductors (unknown) may affect that.
250.122(B) might require an larger EGC if you phase conductors are oversized.
As per 250.122, size of an equipment grounding conductor for a 400 amp circuit is #1 Aluminum.
Steve, you want to ask him why.
A FEEDER CONTAINS SIX ALUMINUM CONDUCTORS INSTALLED IN (A) PVC CONDUIT. TWO CONDUCTORS PER PHASE ARE PROTECTED BY A 400 AMP FUSE. WHAT SIZE ALUMINUM EQUIPMENT GROUNDING CONDUCTOR IS REQUIRED?
 