I have a question I never thought I would have to ask here.
I have 3 solar arrays recently built by a reputable contractor that have no EGC in any of the string wire conduits. This is a ground mount array, fixed tilt with Chint String inverters back at the pad area.
Every row has a GEC conductor running back to the 4/0 ground ring at the pad, and the EC is claiming that this can substitute for the EGC in each conduit. There is an EGC in the AC feeder pipe to the inverters, from the Main disconnect at the pad.
I have wired thousands of structures, built over a GW of solar projects all over the US, hold a Master Electricians license in MA, NH, DE, UT and never have I ever seen an EC not run the EGC in the pipe with the branch circuits (unless the conduit can serve as the grounding means).
The EC is citing 690.43(C)
Isn't there a clear code requirement that every raceway that has CCC must have a grounding conductor in it? Or have we all just been wasting wire for decades now?
thanks in advance for all your advice.
I have 3 solar arrays recently built by a reputable contractor that have no EGC in any of the string wire conduits. This is a ground mount array, fixed tilt with Chint String inverters back at the pad area.
Every row has a GEC conductor running back to the 4/0 ground ring at the pad, and the EC is claiming that this can substitute for the EGC in each conduit. There is an EGC in the AC feeder pipe to the inverters, from the Main disconnect at the pad.
I have wired thousands of structures, built over a GW of solar projects all over the US, hold a Master Electricians license in MA, NH, DE, UT and never have I ever seen an EC not run the EGC in the pipe with the branch circuits (unless the conduit can serve as the grounding means).
The EC is citing 690.43(C)
Isn't there a clear code requirement that every raceway that has CCC must have a grounding conductor in it? Or have we all just been wasting wire for decades now?
thanks in advance for all your advice.