I am replacing 4 aged panels in a commercial building. All panels are fed from separate overcurrent devices in a cabinet on the exterior of the building. Each panel is fed through either rigid or EMT conduit through the space above a t-bar grid ceiling, and load-end cabinet connections are through concentric knock-outs in the top of the panel.
These panels were dated back to the early '60's and I don't know what Code requirements were back then, but have been searching for any article 250 requirements pertaining to whether or not I need to run a separate EGC through the entire length of conduit run from cabinet to cabinet (switch gear to load end). I am planning on adding grounding bushings and the proper-sized bonding jumper in the individual panels, as none are present and the K.O.s are not fully broken out.
One of the panels is three-phase, and is fed merely with the ungrounded conductors, relying only on the conduit as the ground connection back to the main switch gear.
I do see in 250.8(A)(7) the term "listed assembly", which I suppose could pertain to connectors between conduit sections and related fittings, however I am looking to have one inspection when I am done and to be able to have confidence that I added the proper "upgrades" to the system.
Thanks for any input on this post.
Bob
These panels were dated back to the early '60's and I don't know what Code requirements were back then, but have been searching for any article 250 requirements pertaining to whether or not I need to run a separate EGC through the entire length of conduit run from cabinet to cabinet (switch gear to load end). I am planning on adding grounding bushings and the proper-sized bonding jumper in the individual panels, as none are present and the K.O.s are not fully broken out.
One of the panels is three-phase, and is fed merely with the ungrounded conductors, relying only on the conduit as the ground connection back to the main switch gear.
I do see in 250.8(A)(7) the term "listed assembly", which I suppose could pertain to connectors between conduit sections and related fittings, however I am looking to have one inspection when I am done and to be able to have confidence that I added the proper "upgrades" to the system.
Thanks for any input on this post.
Bob