housemoney
Member
- Location
- Midwest
- Occupation
- Engr
A facility has a number of 75 kVA 480V:120/208V step down XFMRs located in close proximity to high load concentration areas. All these XFMRs are using the EGC as the only grounding electrode conductor. Most of these EGC's have only one connection to a grounding electrode back where they originate, hundreds of feet away in an electrical room. I understand this is OK per 250.121-exception.
However- There are no other GECs connected to the XFMRs ground bus locally- building steel, metal process piping or cable tray ( which is bonded to building steel in areas) is available near all of them.
This facility has a history of electrical disturbances associated with these SDS sources (which are all grounded correctly other than my concern above) in a high lightning prone area (building is equipped with a lighting protection system but needs to be inspected). Would it be advisable/ good practice to install a dedicated GEC from a local grounding electrode to the ground bus of these transformers to potentially limit / stabilize the voltage imposed by line surges or other disturbances?
However- There are no other GECs connected to the XFMRs ground bus locally- building steel, metal process piping or cable tray ( which is bonded to building steel in areas) is available near all of them.
This facility has a history of electrical disturbances associated with these SDS sources (which are all grounded correctly other than my concern above) in a high lightning prone area (building is equipped with a lighting protection system but needs to be inspected). Would it be advisable/ good practice to install a dedicated GEC from a local grounding electrode to the ground bus of these transformers to potentially limit / stabilize the voltage imposed by line surges or other disturbances?