Electromatic
Senior Member
- Location
- Virginia
- Occupation
- Master Electrician
I'm trying to confirm the proper EGC size for a service that will be partially temped-in during construction. It's a bit of an oddball, though. There is an existing 200A feeder run a long distance to a pole-mounted disconnect that then continues a short distance to a small pumping building. The temp service will be from the pole disconnect to the building. The long run is using 2 sets of 250kcmil Aluminum in (2)3"RMC conduits with the conduits acting as the EGC.
For the new temp from the pole to the building, I think a single run of 250kcmil (205A) will be okay. Can I just base the EGC size on that portion of the run on the 200A OCPD and use #6Cu/#4Al?
For the new temp from the pole to the building, I think a single run of 250kcmil (205A) will be okay. Can I just base the EGC size on that portion of the run on the 200A OCPD and use #6Cu/#4Al?