Red tagged in northern Michigan for “Undersized “ equipment grounding conductor on a 200 amp feeder.
Inspector sited 3603.1 of the Michigan residential code. service, feeder, and grounding electrode conductor sizing is the name of the paragraph header
I installed a #6 EGC for a 200 amp feeder from a main service rated generac transfer switch to a 200 amp sub panel. Inspector said I need to run a #4 copper EGC. Of course he calls it a grounding electrode cunductor
Looking for help on how to nicely explain to the inspector his error