This is existing HVAC outside unit
MCA 23.3 amps
MCA 40
Installer ran 10 AWG THHN from 30 amp breaker, with #12 EGC
I added a j box in feed to HVAC outside unit
I think the EGC should be #10?
Or I could refeed with #12 THHN which is how I would of done it my self