Do you need to size the EGC on HVAC circuits to match the size breaker installed, or size by MCA? I don't see any exemptions in 250.122 for article 440 circuits, but there is a limited one for article 430 motors.
It would seem logical to size by MCA and not the breaker which is usually a size or two above what you'd install for MCA. If that idea is wrong, this could also force you to upsize when using a cabling method if the MCA is 20A but the breaker is 30A.
I can't find any code to back this notion up. Is there any?
It would seem logical to size by MCA and not the breaker which is usually a size or two above what you'd install for MCA. If that idea is wrong, this could also force you to upsize when using a cabling method if the MCA is 20A but the breaker is 30A.
I can't find any code to back this notion up. Is there any?