EGC Size question

Status
Not open for further replies.

hochwire

Member
Location
Kansas
Occupation
Electrical Project Manager
On a recent project a motor starter panel required 250A 480V feeder, so I installed 2" IMC with 3 250MCM copper conductors and a #4 copper ground wire, now thw owner wants to increase the feeder to 400A to pickup some additional loads being installed, my intension is to run another 2" IMC and parrell 3 more 250MCM copper conductors, but the #4 copper ground wire installed in the first conduit is to small for 400A according to table 250.122. The conduits are about 300 feet long may be able to pull the #4 out and pull in a larger EGC conductor if it is necessary or can use the conduit as the ground? Or what other options are there?
 
Options:

1. pull out the existing 4 AWG and install the 3 AWG in each raceway as per 250122(F

2. pull out the existing 4 AWG and use the raceways as your EGC.

3. Abandon the original 4 AWG EGC (make sure to safe it off - tape, wirenuts, etc... and I would tag it as abandoned), and use the raceways as your EGC.
 