On a recent project a motor starter panel required 250A 480V feeder, so I installed 2" IMC with 3 250MCM copper conductors and a #4 copper ground wire, now thw owner wants to increase the feeder to 400A to pickup some additional loads being installed, my intension is to run another 2" IMC and parrell 3 more 250MCM copper conductors, but the #4 copper ground wire installed in the first conduit is to small for 400A according to table 250.122. The conduits are about 300 feet long may be able to pull the #4 out and pull in a larger EGC conductor if it is necessary or can use the conduit as the ground? Or what other options are there?