shivam.pandey
Member
- Location
- Chula Vista
- Occupation
- Solar design engineer
I am working on a PV project and need to size EGC for circuit after DC combiner box. Module Isc is 13.95A. Considering 8.4% bifacial gain effective Isc would be 15.12A. Now per (690.8(A)(1)(1)) Isc would become 18.90A. Now again per (A) (690.8(B)(1)), Isc*1.25 would be 23.63A. We have 12 strings paralleled and total current from the output of the combiner would be 12*23.63=283.5A
Isc= 13.95A
With bifacial gain = 13.95*1.084= 15.12A
Total current at combiner box = 12 strings * 15.12= 181.44A
Now per NEC 181.44*1.56=283.05A
Should I use 300A for the OCPD as this is the next standard OCPD size for EGC sizing or use max disconnect rating of DC combiner box i.e 400A (Combiner is rated for the 400A with 400A disconnect switch).
With 300A, EGC would be 2 AWG and with 400A would be 1 AWG for aluminum conductor.
Isc= 13.95A
With bifacial gain = 13.95*1.084= 15.12A
Total current at combiner box = 12 strings * 15.12= 181.44A
Now per NEC 181.44*1.56=283.05A
Should I use 300A for the OCPD as this is the next standard OCPD size for EGC sizing or use max disconnect rating of DC combiner box i.e 400A (Combiner is rated for the 400A with 400A disconnect switch).
With 300A, EGC would be 2 AWG and with 400A would be 1 AWG for aluminum conductor.