Can someone help with this. I keep getting cross referenced and and conflicting code articles no jiving.
RTU with full load at 75 amps 3 phase 208V
Running 1.25 conduit (flex to seal tight) with 3-#3 Cu and 1 - ???? EGC (25 ft run tops)
I'm seeing run same size #3 Cu (seems like overkill) and I'm seeing #6 0r #8 from 250.95
Can someone straighten me out of this once and for all simplified? I'd rather not run 4-#3's if not needed if needed I'll run it
250.122 doesn't have any column for 75 amps, I'm putting on a 3 pole 90 amp breaker and I'm upsizing conductors so RTU has less resistance also
RTU with full load at 75 amps 3 phase 208V
Running 1.25 conduit (flex to seal tight) with 3-#3 Cu and 1 - ???? EGC (25 ft run tops)
I'm seeing run same size #3 Cu (seems like overkill) and I'm seeing #6 0r #8 from 250.95
Can someone straighten me out of this once and for all simplified? I'd rather not run 4-#3's if not needed if needed I'll run it
250.122 doesn't have any column for 75 amps, I'm putting on a 3 pole 90 amp breaker and I'm upsizing conductors so RTU has less resistance also