I have never seen anyone do the calculation to size EGCs correctly anyway.
It must be a large burden being the only good electrician.
Everyone I know just looks up a value in 250.122 and upsizes it if the CCC is upsized. Most people do not even know there is a note on that table that says, "Where necessary to comply with 250.4(A)(5) or (B)(4), the equipment grounding conductor shall be sized larger than given in this table." This table is just a hard minimum, not a way to select the correct size EGC, and by its own admission is not conservative. The only way to correctly size the EGC is to do the fault current impedance calculation and match it to the OCPD trip requirements to make sure the EGC is going to be able to carry enough fault current to trip the OCPD.
The above is your opinion of the code, not every AHJ feels the same way.