Hi brainiacs,
Need some clarification.
I have a 2000 amp 277/480v service to an office building. The 2000 amp transfer switch failed and we are installing a new one. I am going to use the existing transfer switch cabinet as a J-box. I am running 5 parallel 3" conduits for the utility power and 5 parallel 3" conduits for the load side of the transfer switch. Each conduit is going to have 4 - 500 kCmil conductors. What would be the EGC size?
Table 250.122 says 250 kCmil based on the size of the O.C. device.
250.122 (F) (1) (b) says to use table 250.122 for multiple raceways for feeders or branch circuits. Do I not use this table for the main service?
If I do use this table, the last sentence of 250.122(F)(1)(b) states: Metal raceways or auxiliary gutters in accordance with 250.118..........shall be permitted as the equipment grounding conductor.
250.118 (4) Says EMT can be used as an EGC.
Does this mean that I do not need to install a separate EGC in the conduit?
Need some clarification.
I have a 2000 amp 277/480v service to an office building. The 2000 amp transfer switch failed and we are installing a new one. I am going to use the existing transfer switch cabinet as a J-box. I am running 5 parallel 3" conduits for the utility power and 5 parallel 3" conduits for the load side of the transfer switch. Each conduit is going to have 4 - 500 kCmil conductors. What would be the EGC size?
Table 250.122 says 250 kCmil based on the size of the O.C. device.
250.122 (F) (1) (b) says to use table 250.122 for multiple raceways for feeders or branch circuits. Do I not use this table for the main service?
If I do use this table, the last sentence of 250.122(F)(1)(b) states: Metal raceways or auxiliary gutters in accordance with 250.118..........shall be permitted as the equipment grounding conductor.
250.118 (4) Says EMT can be used as an EGC.
Does this mean that I do not need to install a separate EGC in the conduit?