EGC sizing
schole
When upsizing circuits to compensate for voltage drop the egc size needs to be considered as per 250.122 (B). Is there a quicker means of determining an appropriate ground size than applying the formula and checking the tables ? Rule of thumb, does going to the next size down in conductor size cover the EGC sizing requirement?
If the original size of the conductor was either 14, 12, or 10 gauge then the ratio is one to one. Thus a #14, 12 or 10 wire gets upsized to #6 then the egc must also be #6. There is no rule of thumb for the other but it only takes a minute to figure it out. Do you need help with that?