... Jaggedben can give you all the details from each code cycle, he's an expert in that and I always forget the specifics.
Briefly...
UL standards require a 'GEC' terminal for inverters with a grounded DC conductor, but not those without. 690 was originally written on the assumption that a GEC would be required, and was a bit slow to catch up as ungrounded systems became the norm.
The NEC until 2011 required that GEC to be installed to the same standard as GECs elsewhere in the code, more or less.
The 2014 NEC allowed the GEC for an ungrounded system to be sized the same as an EGC, but didn't explicitly remove the other GEC installation standards (continuous, bonded both ends, etc.). It still refers to it as a GEC.
The 2017 dispenses with the GEC language except for solidly grounded systems, which are old-hat. (A really basic off-grid system that doesn't serve a building is probably the only type that might still be solidly grounded if installed today.) Typical PV systems under the 2017 NEC can just use EGCs everywhere. The building or structure still needs a grounding-electrode-system, but that's usually true whether there's a PV system or not.
Everything I refer to above is about the GEC for the inverter/PV system, and not the 'array electrode' in 690.47(D) (or (B) in 2017). That's a whole other can of worms.