hello forum this is my first post here ive been a longtime lurker , my name is steve . im not sure if im in the right spot of the forum or if i have titled this properly . i work for a company that provides installation and repairs to fire apparatus line voltage systems , i also deal with electrical maintence at my companys shop and offices . they have a Jman on staff but he is a real pita to deal with .
Heres the situation . They have a smaller building approx 500 feet from the main shop that is used as the welding and fabrication area .
currently they have power pulled out of the main panel on a 50 amp 2 pole CB 240v single phase . there is duplex air compressor in the welding area 2 240v single phase motors @ 5hp 28amps each , yes i know grossly overloaded at that , then they run a plasma cutter at the same time and cant seem figure out why the breaker trips , they just whine that they have to walk so far to reclose the cb
so basically i went to the jman and told him we needed to run new feeders for the sub at the weld shop , his solution was to pull 3
4 ought aluminum cables in line 1 line 2 neutral which for voltage drop sounds reasonable to me i havent done the math yet.
my issue with this and my question is , isnt there a egc required in the conduit with the feeders , when i asked the jman he anwser was drive 2 new ground rods , and connect the gec and bond the neutral and ground bar in the sub . it sounds fishy to me and i have had trouble locating the section in the nec that covers that
Heres the situation . They have a smaller building approx 500 feet from the main shop that is used as the welding and fabrication area .
currently they have power pulled out of the main panel on a 50 amp 2 pole CB 240v single phase . there is duplex air compressor in the welding area 2 240v single phase motors @ 5hp 28amps each , yes i know grossly overloaded at that , then they run a plasma cutter at the same time and cant seem figure out why the breaker trips , they just whine that they have to walk so far to reclose the cb
so basically i went to the jman and told him we needed to run new feeders for the sub at the weld shop , his solution was to pull 3
4 ought aluminum cables in line 1 line 2 neutral which for voltage drop sounds reasonable to me i havent done the math yet.
my issue with this and my question is , isnt there a egc required in the conduit with the feeders , when i asked the jman he anwser was drive 2 new ground rods , and connect the gec and bond the neutral and ground bar in the sub . it sounds fishy to me and i have had trouble locating the section in the nec that covers that