HRG is monitored
HRG is monitored
I agree that if there is one phase-ground fault then the HRG will limit fault current. If there is a second phase-ground fault involving a different phase, then the fault current could go through the EGC. However, the HRG is monitored in an industrial application so that once the first fault occurs, there is an alarm. The HRG is meant to reduce the damage caused by a phase-ground fault.
Also, I am not concerned about the size of the bonding jumper from a metal enclosure to the EGC but rather the size of the EGC used in parallel PVC underground conduits on a feeder from the switchgear to the MCC. See attached.
In this case there is a 480Y/277V transformer with 10A HRG as part of a unit substation located several hundred feet from the MCC. There are three or four parallel PVC conduits from the unit substation switchgear to the MCC. Since I have a 1200A trip breaker, am I required to install a 3/0 copper EGC in each PVC conduit? Reality is that there is no fault that will ever require the rating of the 3/0 parallel conductors to be needed.
The argument that if there is a 2nd phase-ground fault in the MCC that the EGC back to the unit substation comes into play does not work because the fault would become phase-phase in the MCC and there would not be high current back to the unit substation.
This is a great learning process and I appreciate all the input.