In European countries do they use the grounded conductor as a EGC ?
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Generally no.
And instead of EGC they call it PE for Protective Earth.
They care a lot about having a low impedance local GES too, because at 240V and up it can be a usable fault clearing path. Unlike our 25 ohm GES which at 120V can't even trip a 15A breaker.
 

MMT77002

Member
Location
Houston, TX USA
EGC on IEC Systems

EGC on IEC Systems

Generally no.
And instead of EGC they call it PE for Protective Earth.
They care a lot about having a low impedance local GES too, because at 240V and up it can be a usable fault clearing path. Unlike our 25 ohm GES which at 120V can't even trip a 15A breaker.

I worked a lot with IEC systems in the past - Sorry to say the answer depends on the country where the installation occurs - local utilities will typically the requirements. There are three basic systems (and alternatives) - TN, TT and IT. Without going into some long winded explanation this is a graphical representation:

http://www.electrical-installation.org/enwiki/Earthing_schemes_(_full_page_)

Remember the voltages can be 415Y/240v (British) or 380Y/220v (Continental Europe) The Middle East and Asian countries are a mix of both.

Hope this helps
 