6 618electrician Member Location St. Louis Occupation Maintenance electrician Apr 24, 2025 #1 Can i use one EGC and wire nut 4 to it and take it to the ground block ? ( if i dont have a room on the ground buss )
Can i use one EGC and wire nut 4 to it and take it to the ground block ? ( if i dont have a room on the ground buss )
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Apr 24, 2025 #2 Yes. The pigtail would be sized for the largest EGC within the splice.