I have a 4.16kv chiller that has RGSC from switchgear to 3' above connection box. Then it transistions to LFMC (< 6') to the connection box. Is an EGC required to be run with the feeder cables or can the conduit be the EGC? Per 250.118, (6)e, it appears as though it is required.