joeyww12000
Senior Member
- Location
- Chatsworth GA
Just to make sure if Im understanding ground fault current path correct. If I have a 120v 2 wire circuit and a 277v 2 wire circuit in the same conduit I must have 2 EGC's for each system. The reason I ask is some older more experienced electricians I know pull one EGC, making me second guess my knowledge. Maybe one EGC is OK but it must be spliced and terminated in each panel, so a ground fault can return to each systems power source? If I pulled one EGC and had a ground fault from the 277v circuit and the EGC was only connected in the 120v panel this would not allow the OCPD in the 277v panel to open up?