Do any of you have pictures or catalog numbers for fixtures that you have used to comply with 1006.3 of the IBC?
1006.3 Illumination emergency power. The power supply for
means of egress illumination shall normally be provided by the
premises? electrical supply.
In the event of power supply failure, an emergency electrical
system shall automatically illuminate all of the following
areas:
1. Aisles and unenclosed egress stairways in rooms and
spaces that require two or more means of egress.
2. Corridors, exit enclosures and exit passageways in
buildings required to have two or more exits.
3. Exterior egress components at other than their levels of
exit discharge until exit discharge is accomplished for
buildings required to have two or more exits.
4. Interior exit discharge elements, as permitted in Section
1027.1, in buildings required to have two or more exits.
5. Exterior landings as required by Section 1008.1.6 for exit
discharge doorways in buildings required to have two or
more exits.
The emergency power system shall provide power for a
duration of not less than 90 minutes and shall consist of storage
batteries, unit equipment or an on-site generator. The installation
of the emergency power system shall be in accordance
with Chapter 27.
For those not familiar with the IBC I will post section 1006.3
A lot of times I use an emergency battery pack installed in a standard fluorescent fixture.
Chris
The main reason for my question is or maybe the real question is, is anyone even doing it? I have yet to see it on a set of plans.
John,
Should that get 'caught' by the Plans Examiner ? In the Phoenix area, we have been installing them for quite a few years now. We also have used the fixture Joe V posted as
well as two headed outdoor rated EM units.