how many exit doors for emergency egress is required for an electrical room with a 2000 amp 480 volt switchboard/motor control center, & what section of the
2017 nec code shows this
 

d0nut

Senior Member
Location
Omaha, NE
It depends on the configuration of the room. A minimum of one would be required, but you could need more depending on how the equipment and the room is laid out. The requirements are in 110.26.
 