ItsHot said:
You may need dedicated circuits, so you do not have "something very screwy" with the neutrals!:grin:
This may not solve the issue. If there is ground current the new cable EGC may/will carry some of the ground current.
If you have neutral ground issues you need to locate them.
1. Do you have a Gauss meter?
2. Use the Gauss meter to check for EMFs, a good sign of neutral issues.
3. Use a clamp on and take zero sequence measurements on the panel feeders all phase and neutral simultaneously, the reading should be ZERO "0".
4. Measure current on the neutral to ground bond jumper. This should be "0" or close to "0".
5. With the power off, lift all branch circuit neutrals.
6. Unplug all equipment and turn off all lights.
7. Megger the neutrals to ground at 100 VDC then 1000 VDC, an ohm meter will suffice but a megger is perfered.
8. All neutrals that megger "0" or have questionable readings should be investigated.