Are you sure it monitors current on the EGC? I did a quick search and didn't find anything yet on how they work, but I would think they would be better off using same technology as a GFCI. They could certainly use a different current level for the trip threshold though. If you lost the EGC for any reason, or never had one to start with, the GFCI technology still will work should current find some other leakage path, but the method you describe likely doesn't see any leakage in that instance because nothing is flowing in the intended EGC in the supply cord.Not sure about marine installations, but I know earth leakage detectors are common as appliance plugs for window ACs and some older hair dryers.
They monitor the ground wire from the appliance. Should it develop a potential between the hot and neutral or neutral and ground out of spec or it senses excessive current flow through the EGC it opens up the hot and neutral or both hots in the case of 240. Its different from a GFCI in that a GFCI has a ct and looks for current differential between the 2 conductors rather than current or voltage anomalies on the EGC.
Of course Im thinking more along the lines of a cord and plug ELCI than what might be used on marine power.
There are a variety of GFCI-like devices out there, made for use as part of specific listed equipment. For example, window air conditioners have their "LCDI," and hair dryers have their gizmo.
Then there's the use overseas of the "RCD" at the service entrance.
There are AFCI's, which supposedly also have a GFCI component - but are NOT approved for use as GFCI's
Finally, there are specialty GFCI's with trip levels different from the usual 4-6mA setting of the ordinary GFCI.
I don't know anything about the item you name - but the code says GFCI, so GFCI it must be.