Permanent Installed Residential Optional Stand-By Systems
in accordance with 2002 National Electrical Code
I. Article 702 Optional Stand-By Systems
702.1 Scope.
The provisions of this article apply to the installation and operation of optional standby systems.
The systems covered by this article consist of those that are permanently installed in their entirety, including prime movers, and those that are arranged for a connection to a premises wiring system from a portable alternate power supply.
The scope of Article 702 was revised for the 2002 NEC to clarify that it applies not only to permanently installed generators and prime movers, but also to portable alternate power supplies that can be connected to an optional standby system. For example, upon failure of an optional standby generator at a frozen food processing plant, a vehicle-mounted generator can be brought in and connected to the plant's optional standby system, which has provisions for such a connection.
Optional standby systems are those in which failure can cause physical discomfort, serious interruption of an industrial process, damage to process equipment, or disruption of business.
702.2 Definition.
Optional Standby Systems. Those systems intended to protect public or private facilities or property where life safety does not depend on the performance of the system. Optional standby systems are intended to supply on-site generated power to selected loads either automatically or manually.
FPN: Optional standby systems are typically installed to provide an alternate source of electric power for such facilities as industrial and commercial buildings, farms, and residences and to serve loads such as heating and refrigeration systems, data processing and communications systems, and industrial processes that, when stopped during any power outage, could cause discomfort, serious interruption of the process, damage to the product or process, or the like.
702.3 Application of Other Articles.
Except as modified by this article, all applicable articles of this Code shall apply.
702.5 Capacity and Rating.
An optional standby system shall have adequate capacity and rating for the supply of all equipment intended to be operated at one time. Optional standby system equipment shall be suitable for the maximum available fault current at its terminals. The user of the optional standby system shall be permitted to select the load connected to the system.
II. Optional Calculations for Computing Feeder and Service Loads
220.30 Optional Calculation — Dwelling Unit.
(A) Feeder and Service Load. For a dwelling unit having the total connected load served by a single 3-wire, 120/240-volt or 208Y/120-volt set of service or feeder conductors with an ampacity of 100 or greater, it shall be permissible to compute the feeder and service loads in accordance with this section instead of the method specified in Part II of this article. The calculated load shall be the result of adding the loads from 220.30(B) and (C). Feeder and service-entrance conductors whose demand load is determined by this optional calculation shall be permitted to have the neutral load determined by 220.22.
(B) General Loads. The general calculated load shall be not less than 100 percent of the first 10 kVA plus 40 percent of the remainder of the following loads:
(1) 1500 volt-amperes for each 2-wire, 20-ampere small-appliance branch circuit and each laundry branch circuit specified in 220.16.
(2) 33 volt-amperes/m2 or 3 volt-amperes/ft2 for general lighting and general-use receptacles. The floor area for each floor shall be computed from the outside dimensions of the dwelling unit. The computed floor area shall not include open porches, garages, or unused or unfinished spaces not adaptable for future use.
(3) The nameplate rating of all appliances that are fastened in place, permanently connected, or located to be on a specific circuit, ranges, wall-mounted ovens, counter-mounted cooking units, clothes dryers, and water heaters.
(4) The nameplate ampere or kVA rating of all motors and of all low-power-factor loads.
(C) Heating and Air-Conditioning Load. The largest of the following six selections (load in kVA) shall be included:
(1) 100 percent of the nameplate rating(s) of the air conditioning and cooling.
(2) 100 percent of the nameplate ratings of the heat pump compressors and supplemental heating unless the controller prevents the compressor and supplemental heating from operating at the same time.
(3) 100 percent of the nameplate ratings of electric thermal storage and other heating systems where the usual load is expected to be continuous at the full nameplate value. Systems qualifying under this selection shall not be calculated under any other selection in 220.30(C).
(4) 65 percent of the nameplate rating(s) of the central electric space heating, including integral supplemental heating in heat pumps where the controller prevents the compressor and supplemental heating from operating at the same time.
(5) 65 percent of the nameplate rating(s) of electric space heating if less than four separately controlled units.
(6) 40 percent of the nameplate rating(s) of electric space heating if four or more separately controlled units.
220.31 Optional Calculations for Additional Loads in an Existing Dwelling Unit.
This section shall be permitted to be used to determine if the existing service or feeder is of sufficient capacity to serve additional loads. Where the dwelling unit is served by a 120/240-volt or 208Y/120-volt, 3-wire service, it shall be permissible to compute the total load in accordance with 220.31(A) or (B).
(A) Where Additional Air-Conditioning Equipment or Electric Space-Heating Equipment Is Not to Be Installed. The following formula shall be used for existing and additional new loads.
Load (kVa) Percent of Load
First 8 kVA of load at 100
Remainder of load at 40
Load calculations shall include the following:
(1) General lighting and general-use receptacles at 33 volt-amperes/m2 or 3 volt-amperes/ft2 as determined by 220.3(A)
(2) 1500 volt-amperes for each 2-wire, 20-ampere small-appliance branch circuit and each laundry branch circuit specified in 220.16
(3) Household range(s), wall-mounted oven(s), and counter-mounted cooking unit(s)
(4) All other appliances that are permanently connected, fastened in place, or connected to a dedicated circuit, at nameplate rating
(B) Where Additional Air-Conditioning Equipment or Electric Space-Heating Equipment Is to Be Installed. The following formula shall be used for existing and additional new loads. The larger connected load of air-conditioning or space-heating, but not both, shall be used.
Air-conditioning equipment 100
Central electric space heating 100
Less than four separately controlled space-heating units 100
First 8 kVA of all other loads 100
Remainder of all other loads 40
Other loads shall include the following:
(1) General lighting and general-use receptacles at 33 volt-amperes/m2 or 3 volt-amperes/ft2 as determined by 220.3(A)
(2) 1500 volt-amperes for each 2-wire, 20-ampere small-appliance branch circuit and each laundry branch circuit specified in 220.16
(3) Household range(s), wall-mounted oven(s), and counter-mounted cooking unit(s)
(4) All other appliances that are permanently connected, fastened in place, or connected to a dedicated circuit, including four or more separately controlled space-heating units, at nameplate rating