Can someone explain to me why an electric oven which spans 208- 240 volt single phase uses 13.4 kw at 240 volt and 10.1 kw at 208 volt . It would seem to be at odds with ohms law. In addition the manufactuer says at either kw the overcurrent is 40 amp. Am I wrong in calculating the amperage at 13,400 divided by 240 = 55 amps and 10000 divided by 208 = 48 amps. Thanks in advance.
 
The oven has a fixed (minimum) resistance of approximately 4.3 ohms.

At 240 volts, you get 240V / 4.3 ohms = 55.8A and 240V x 55.8A = ~13.8 kW.

At 208 volts you get 208V / 4.3 ohms = 48.4A and 208 * 48.4A = ~10.1 kW.
 
Congress repealed Ohms law because it was biased against the ignorant. :dunce: They didn't know what the law was about ( they never read those things ) but the knew they didn't like it ( no special interest money ).
 
40 amp breaker for both?

Protects the #8 copper conductor feeding the range.


The range will never operate at 100% capacity or that 55 amp, at least not long enough to worry about.

I am surprised they didn't specify a 50 amp circuit for the range but you will have to take that up with the manufacturer.

I have seen a few ranges that did require a 50 amp circuit but very few.
 
Can someone explain to me why an electric oven which spans 208- 240 volt single phase uses 13.4 kw at 240 volt and 10.1 kw at 208 volt . It would seem to be at odds with ohms law. In addition the manufactuer says at either kw the overcurrent is 40 amp. Am I wrong in calculating the amperage at 13,400 divided by 240 = 55 amps and 10000 divided by 208 = 48 amps. Thanks in advance.

As DFM stated your math was incorrect because you need to use the resistance with ohms law. Also as Jumper stated you can use T220.55 to apply a demand factor which may get you branch circuit down to 40 amps even if the the unit is 13.4 kw.
 