Everyone, I posted here last time i had a project and got a lot of good experience from everyone and this time i'd like some more. If everyone could be so kind.
The Problem:
We are a 35MW electric arc furnace. Our arc furnace transformer is 45MVA 13.8kv to 800V secondary. We use 18" electrodes running about 30-35,000 amps with a online tap changer from 500-800V. We are having issues buying electrodes in the 18" range and are thinking of running 24" electrodes, they are significantly cheaper and more available.
We control the current via how much we dip the electrodes into the scrap/metal. Changing from 18" to 24" will significantly change how we arc, and throttle our current. It will also change how hot the electrodes get. What i am afraid of is that we will reduce the resistance and allow for higher current spikes to hit our transformer thus damaging it. I am also afraid of the electrode not responding correctly as it will be significantly under powered. I know that this entire system was engineered to be this way but in order to keep doors open we are looking at all avenues.
Another road I would also like to consider is switching our furnace from AC to DC. This would go from 3 electrodes to 1. The reduction of electrode surface area would reduce our electrode consumption as oxidation is our biggest waste. I know several furnaces have switched in the past, but i don't know what benefits it has for them or even if its worth it for us.
Anyway just peoples thoughts on electrode size change and/or AC to DC Arc Furnace conversion.
PS:
I understand that these projects cost a lot of money but at the moment this is brain storming and there are no stupid ideas!:thumbsup:
The Problem:
We are a 35MW electric arc furnace. Our arc furnace transformer is 45MVA 13.8kv to 800V secondary. We use 18" electrodes running about 30-35,000 amps with a online tap changer from 500-800V. We are having issues buying electrodes in the 18" range and are thinking of running 24" electrodes, they are significantly cheaper and more available.
We control the current via how much we dip the electrodes into the scrap/metal. Changing from 18" to 24" will significantly change how we arc, and throttle our current. It will also change how hot the electrodes get. What i am afraid of is that we will reduce the resistance and allow for higher current spikes to hit our transformer thus damaging it. I am also afraid of the electrode not responding correctly as it will be significantly under powered. I know that this entire system was engineered to be this way but in order to keep doors open we are looking at all avenues.
Another road I would also like to consider is switching our furnace from AC to DC. This would go from 3 electrodes to 1. The reduction of electrode surface area would reduce our electrode consumption as oxidation is our biggest waste. I know several furnaces have switched in the past, but i don't know what benefits it has for them or even if its worth it for us.
Anyway just peoples thoughts on electrode size change and/or AC to DC Arc Furnace conversion.
PS:
I understand that these projects cost a lot of money but at the moment this is brain storming and there are no stupid ideas!:thumbsup: