I would like to clarify with anyone that i'm am sizing my conductors and ocpd for a residential welder correctly.
The name plate states that the primary current is 48 amps, the supply is 240 VAC and the duty cycle on the lower amp range is 100% and 20% on the higher amp range(120 - 230amps).
Using article 630 for ampacity of supply conductors, i assume i would use 100% duty cycle in table 630.11(a) giving me primary current x 100% = 48 amps.
For the ocpd 630.12(a) states that it should not exceed 200% of the primary current - 48 x 200% = 96 amps (use a 90 amp breaker).
I would like to know is this correct or could you use a smaller breaker because the welding plug is a three prong 240V 50 amp plug on a number 10 awg cord to the welder. Could you use a 50 or 60 amp breaker?
Any help would be appreciated.