Eddie702
Licensed Electrician
- Location
- Western Massachusetts
- Occupation
- Electrician
I have read article 424 and as far as I can see it requires (and always has) that baseboard thermostats need an "off" position as required in 424.19 & 424.20. I have no problem with that.
But I have seen a bunch of digital baseboard thermostats (both by Honeywell & White Rogers) that are single pole and have no "off" position. I would assume these cannot be used as a disconnect.
I had a customer that bought some of these for me to install but with no disconnect ability and single pole I don't see any way they can be used.
The only loophole I see is if the branch circuit breaker can be locked off as mentioned in 424.19 sec 110.25
Am I missing something??
How can the MFG. put these out?
But I have seen a bunch of digital baseboard thermostats (both by Honeywell & White Rogers) that are single pole and have no "off" position. I would assume these cannot be used as a disconnect.
I had a customer that bought some of these for me to install but with no disconnect ability and single pole I don't see any way they can be used.
The only loophole I see is if the branch circuit breaker can be locked off as mentioned in 424.19 sec 110.25
Am I missing something??
How can the MFG. put these out?