Hey guys,
I am a little unclear on article 424. for installing electric baseboard heaters so hopefully you guys can clear some things up. Keep in mind this scenario would be for a residential home.
It states that there shall be no receptacles installed above heaters on wall and also the circuit needs to be 125% of its load which I understand.
What I dont get is that the article states that you need a means of disconnect within sight of the heater. This is for a residential home with four apartments. Each apartment has its own service located in basement. There are two apartments on first floor and two apartments on second floor. Each apartment has four 4ft heaters, 4 homeruns total, 16 heaters in total.
My partner is telling me you do not need a disconnect within sight of and that the circuit breaker will be fine although it is in the basement.
1) Am I wrong in thinking that you do in fact need a disconnect?
2) If you do in fact need a disconnect:
Since each apartment's 4 baseboards are located in different rooms within each apartment, do you need a disconnect for each baseboard since they are not exactly with sight of eachother, or will one disconnect be fine for all four?
3) Can a thermostat be considered a disconnect means in this case?
Thanks guys, I really appreciate it.
I am a little unclear on article 424. for installing electric baseboard heaters so hopefully you guys can clear some things up. Keep in mind this scenario would be for a residential home.
It states that there shall be no receptacles installed above heaters on wall and also the circuit needs to be 125% of its load which I understand.
What I dont get is that the article states that you need a means of disconnect within sight of the heater. This is for a residential home with four apartments. Each apartment has its own service located in basement. There are two apartments on first floor and two apartments on second floor. Each apartment has four 4ft heaters, 4 homeruns total, 16 heaters in total.
My partner is telling me you do not need a disconnect within sight of and that the circuit breaker will be fine although it is in the basement.
1) Am I wrong in thinking that you do in fact need a disconnect?
2) If you do in fact need a disconnect:
Since each apartment's 4 baseboards are located in different rooms within each apartment, do you need a disconnect for each baseboard since they are not exactly with sight of eachother, or will one disconnect be fine for all four?
3) Can a thermostat be considered a disconnect means in this case?
Thanks guys, I really appreciate it.