Im adding a 240 kW electric boiler to an independent of the existing electric service. This will be fed from the transformer, to an exterior 700A fused disconnect, and then to an electric boiler located inside the building.
Having an interior non-fused disconnect for service may be an issue due to space because it will be rated for 800A. Anyone see any issue with requiring the exterior disconnect to be lockable in the open position and then providing signage at the boiler notating its power source to eliminate the requirement for an additional disconnect at the boiler itself?
I was thinking of adding a shunt trip inside but this may get expensive.
PS> No, a gas boiler is not an option
Having an interior non-fused disconnect for service may be an issue due to space because it will be rated for 800A. Anyone see any issue with requiring the exterior disconnect to be lockable in the open position and then providing signage at the boiler notating its power source to eliminate the requirement for an additional disconnect at the boiler itself?
I was thinking of adding a shunt trip inside but this may get expensive.
PS> No, a gas boiler is not an option