I have an electric boiler, 480v 3 phase with a nameplate of 441A. For my feeder size to the unit I took 441x1.25% due to continuous duty. This equals 551a minimum conductor ampacity which is paralleled 300’s. (551/2=276a and 300 is good for 285a in the 75c column)
I have a 600a breaker available, an I able to use this or do I need to drop down to a 500 since that would be the next size up from the nameplate of 441A?
There is no mocpd listed on the unit.
I have a 600a breaker available, an I able to use this or do I need to drop down to a 500 since that would be the next size up from the nameplate of 441A?
There is no mocpd listed on the unit.