Master ElectricianThere is no standard. There an multiple options.
What is your profession?
How is it all in 625? It appears that the load would be calculated per 220.14(A) unless adjusted by an automatic load shedding system as provided for in 625.42.It's all in NEC 625.
I don't see anything in (2017) Article 625 that modifies or conflicts with 220.14(A), what am I missing?So 625 takes precedence over 220.14(A). Part III of 625 covers the installation of EV chargers and how to design the branch circuit.
The load calculation is still based on the requirement in 220.14(A) and there is nothing in 625 that changes that, other than the case where the EV changer has load control equipment and the load is permitted to be calculated based on the load control setting. Sure there are installation rules specific to EVs in 625, but this question was about the load calculation and that is in 220.625.40 through .47 provides requirements for the number of branch circuits allowed, over current protection requirements, continuous duty rating requirements, disconnecting means, etc. It's way more and the little blurb in 220.14(A). If someone looks at the charger label for the load amps and uses 220.14(A) to design the branch circuit they are using the NEC incorrectly. This is such a basic concept I can't say anything else about it.