Old service entrance conductors are brittle and need replacement in rigid conduit
The system is red leg. They lost phase A. RED leg in old meter pan ( the terminals are on the bottom and meter on top) is on B phase in meter. Although it should be in C phase I was planning on putting it back where it is on B phase. Some reading I see says B needs 120v for meter.
Leave it on B as it is or switch to C phase.
Second question please. #2 cu thhn/thwn for 100 amp correct.
I measured existing rigid which seems ti measure od 1 3/4
The existing cloth wire measured about 7/8 od
I was going to do #1 bit at the supply house I'm questioning if the existing pipe is 1 1/4 or 1 1/2 ??
I'm good with 2's in either.
2's for 100 amp right ?
Thank you