Hi all,
I was recently given a cut sheet for an electric dryer for an apartment. The cut sheet calls for a 15 amp, 120 volt circuit to feed the dryer.
Usually for electric dryers i see 30 amp, 208 volt circuit requirements that need a NEMA 14-30R receptacle on the wall to feed the dryer. And using the standard calculation, i would use 5,000 watts as a minimum when performing the feeder calculation serving the apartment.
Using the standard calculation method, do I still have to use the 5,000 watt minimum for this type of dryer? The client confirmed with the manufacturer that it is considered an electric dryer. There is no gas connection. But with a 15 amp circuit, this dryer would only be drawing 1000 watts, 1500 watts? Do I still have to go that high with the calculation by using 5000 watts?
I was recently given a cut sheet for an electric dryer for an apartment. The cut sheet calls for a 15 amp, 120 volt circuit to feed the dryer.
Usually for electric dryers i see 30 amp, 208 volt circuit requirements that need a NEMA 14-30R receptacle on the wall to feed the dryer. And using the standard calculation, i would use 5,000 watts as a minimum when performing the feeder calculation serving the apartment.
Using the standard calculation method, do I still have to use the 5,000 watt minimum for this type of dryer? The client confirmed with the manufacturer that it is considered an electric dryer. There is no gas connection. But with a 15 amp circuit, this dryer would only be drawing 1000 watts, 1500 watts? Do I still have to go that high with the calculation by using 5000 watts?