I have an electric fence that was working well until recently. It is mainly to keep dogs in, but there are a few mini donkeys also. There I one energizer (I forget the number of joules, but I think it is 1 joule), 4 acres enclosed and one grounding bar (6' galvanized rod, I think).
When the box is plugged in, it does click, but the light on the box does not light up. When I remove the hot wire and ground wire from the terminals on the enigizer and test the terminals directly, it shows a good signal. Just not when the wires are reconnected. Also, Ill try to make this clear. When
1) The hot wire is connected properly
2) The ground wire is disconnected from the enigizer, but still connected to the grounding bar
3) I then touch the ground wire (the part of the wire that should be connected to the enegizer) to my fence tester ground and the fence works.
All this his is to say, I think my grounding bar is the issue, but not sure why it would suddenly stop working. Any thoughts? Questions to clarify? Suggestions?
Thanks for for any help.
When the box is plugged in, it does click, but the light on the box does not light up. When I remove the hot wire and ground wire from the terminals on the enigizer and test the terminals directly, it shows a good signal. Just not when the wires are reconnected. Also, Ill try to make this clear. When
1) The hot wire is connected properly
2) The ground wire is disconnected from the enigizer, but still connected to the grounding bar
3) I then touch the ground wire (the part of the wire that should be connected to the enegizer) to my fence tester ground and the fence works.
All this his is to say, I think my grounding bar is the issue, but not sure why it would suddenly stop working. Any thoughts? Questions to clarify? Suggestions?