jmd445
Senior Member
- Location
- Hamilton Twp., NJ
Please follow me on this one......
I have a double ended substation, the lay out is as follows.....
15kv disconnect for sub 'A' -> 13.8/480 Transformer 'A' -> main 'A' -> distribution breakers -> tie breaker -> distribution breakers -> main 'B' -> 13.8/480 Transformer 'B' -> 15kv disconnect for sub 'B'
I'm having a new electric fire pump installed and the engineer want's to bug the mains between the transformer 'A' secondary and the Main 'A' circuit breaker. I want a new distribution circuit breaker in a cubicle to feed the fire pump.
This way if I have a failure of either 15kv feeders, disconnects or transformers I can open the main and close the tie and still feed the pump. There will also be a transfer switch to an emergency generator.
My way I have the ability of feeder 'A', feeder 'B' or emergency. The engineer's way I only have Main 'A' or generator.
I realize this is long winded but any thoughts?
Jim
I have a double ended substation, the lay out is as follows.....
15kv disconnect for sub 'A' -> 13.8/480 Transformer 'A' -> main 'A' -> distribution breakers -> tie breaker -> distribution breakers -> main 'B' -> 13.8/480 Transformer 'B' -> 15kv disconnect for sub 'B'
I'm having a new electric fire pump installed and the engineer want's to bug the mains between the transformer 'A' secondary and the Main 'A' circuit breaker. I want a new distribution circuit breaker in a cubicle to feed the fire pump.
This way if I have a failure of either 15kv feeders, disconnects or transformers I can open the main and close the tie and still feed the pump. There will also be a transfer switch to an emergency generator.
My way I have the ability of feeder 'A', feeder 'B' or emergency. The engineer's way I only have Main 'A' or generator.
I realize this is long winded but any thoughts?
Jim