Hi all! Just looked at an electric gate gate job. My first one! Based on what they have this is what I came up with. Will some of you much smarter guys please confirm theses calculations?
126/242 volts at panel
Gate 324 feet away. I figured 330 feet.
Need 7 amps at gate and call box: (2 amp 120 volt Trickle Charger for gate) and (5 amps 240 volt for Call Box). I just figured 10 total.
I'm running UF 6/3 with ground.
Voltage Drop = I x R
“I” is equal to 10 amperes
“R” is equal to 0.324 ohms (Chapter 9, Table 8 for a 6 AWG wire: (.491/1,000 feet) x 660 feet
Voltage Drop = 10 amperes x 0.324 ohms
Voltage Drop = 3.24 volts, (3.24 volts/126 volts = 2.57% volts drop)
Voltage Drop = 3.24 volts, (3.24 volts/242 volts = 1.33% volts drop)
Operating Voltage = 126 volts – 3.24 volts = 122.76
Operating Voltage = 242 volts - 3.24 volts = 238.76
Your help is appreciated!