wireperson
Senior Member
- Location
- Florida
I'll be going to a customer who wants to have a gate in his house. I haven't done a gate b4 .any tips , advices or any inputs about gates?
thanks in advance
thanks in advance
wireperson said:I'll be going to a customer who wants to have a gate in his house. I haven't done a gate b4 .any tips , advices or any inputs about gates?
thanks in advance
LarryFine said:Mr. Persongrin
, I've done a couple. You absolutely must check with the gate supplier/installer on the specifics and locations.
On one, I ran a 1/2" PVC for power (120v) to the 'master' unit, and a 1/2" PVC under the driveway for the 'slave' unit.
On another one, the control was separated from the 'master', so I ran power to the controller, one 1/2" from that to the first post, and one from post to post.
jrannis said:I have done a few but like to keep my underground conduit size as a 1" especially when crossing a driveway.
iwire said:I imagine the inside of 1/2" schedule 80 PVC to be about the size of a pencil.
iwire said:Generally 1" is the smallest I will bury outside, inside I may use 3/4" to floor boxes as many will not take a 1".