Electric hand dryers in school bathrooms

Status
Not open for further replies.

dime

Member
My question concerns the correct type of circuit breaker to use with electric hand dryers in school bathrooms. When a hand dryer is within 6 feet of a sink or even in the sink area is it required to be protected by a GFI circuit breaker? I work in maintenance at a local school district and have seen after engineered building renovations over the past several years were some buildings have GFI circuit breakers and some have standard circuit breakers.
 
Re: Electric hand dryers in school bathrooms

210.8 B (1) GFCI protection which you can get either from the GFCI over current device or a GFCI receptacle.
 
Re: Electric hand dryers in school bathrooms

Originally posted by 110.12:
210.8 B (1) GFCI protection which you can get either from the GFCI over current device or a GFCI receptacle.
110.12 What Ryan is getting at is that if the item is hardwired or happens to be 208-240 no GFCI protection is required.

I believe dime's question is about wall mounted electric hand dryers they are usually (always) hardwired. :)
 
Re: Electric hand dryers in school bathrooms

Sorry, for not suppling more details about these hand dryers. We have three schools all with wall mounted hand dryers. These dryers are 2300 watt/120vac units direct wired to the panel with #10 THHN. One school has 20 amp GFI circuit breakers another school has 20 amp standard circuit breakers and the third school has 30 amp standard circuit breakers. If any of these dryers are within six feet of a sink are they required to be protected by a GFI circuit breaker?
 
Re: Electric hand dryers in school bathrooms

Originally posted by dime:
Sorry, for not suppling more details about these hand dryers. We have three schools all with wall mounted hand dryers. These dryers are 2300 watt/120vac units direct wired to the panel with #10 THHN. One school has 20 amp GFI circuit breakers another school has 20 amp standard circuit breakers and the third school has 30 amp standard circuit breakers. If any of these dryers are within six feet of a sink are they required to be protected by a GFI circuit breaker?
If they are hard wired, no. See Ryan's answer.
If they are cord and plug connected and on a 20 amp breaker, yes. And it doesn't matter how close to the sink they are. See 210.8(B)(1). If they're on a 30 amp breaker, no. But are the receptacle and the dryer suitable for 30 amp circuits?
 
Re: Electric hand dryers in school bathrooms

I design these all the time. Many of the dryers, recommend a GFI breaker. Check with manufacturer. I usually go with GFI breakers to be safe.
 