lmfao !!!! I think what he means is baseboard calcs: No matter what type of inductive heating load you must multiply by 1.25 and remember to omit from the service or feeder calculation the smaller of the Air conditioning and heat. Example AC air handler with compressor 7.2kw with heat at: 20kw drop the 7.2 all together and take 20k X 1.25 = 25kw
If your sizing branch circuits for baseboard you can use 15, 20, or even 30 amp branch circuits so for a branch circuit with 5 - 1250watt units it's 5X1250 = 6250 plus 125% = 7812 / 240 = 32 amps serve with 2 20 amp 240v branch circuits, if your load came just under 30 after your multiplier like 29.3 amps, you could use (1) 30 amp 240v branch circuit. Jim
Note: Using #10 in the stats boxes sucks and takes up a lot more cubic volume and would in some cases cause box over fill.......