When calculating loads for a feeder Art 220.51 states to calculate the fixed electrical heating load at 100%. Art 424.3 states electric heat to be considered a continuous load for branch circuit sizing. In the commentary following 424.3 it also states the the revision for electric heat as a continuous load also applies to the service and feeder calculations.
By code, would I consider the feeder for 100% and branch circuits at 125%?
Comments/suggestions. The 125% would actually be the difference between a 1000A feeder and a 1200A feeder thru an existing building.
Thanks
By code, would I consider the feeder for 100% and branch circuits at 125%?
Comments/suggestions. The 125% would actually be the difference between a 1000A feeder and a 1200A feeder thru an existing building.
Thanks