Electric Heater Equipment Circuit

faresos

Senior Member
Question, NEC 424.4 (A) states "Branch circuits supplying two or more outlets for fixed electric space-heating equipment shall be rated not over 30 amperes.", does this mean I can power two heaters from 30A circuit without the need to provide a fused disconnect (using tap rule) at each unit?

Thank you!
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Question, NEC 424.4 (A) states "Branch circuits supplying two or more outlets for fixed electric space-heating equipment shall be rated not over 30 amperes.", does this mean I can power two heaters from 30A circuit without the need to provide a fused disconnect (using tap rule) at each unit?

Thank you!
Yes
 