Re: Electric Meter/Gas Meter Location
Charlie our poco`s here will not set a meter if there is a gas meter/vent within 3 ft. of the meter base.Not an NEC issue but a poco issue.We usually wire after gas is installed since we have to bond to the gas system but sometimes due to schedulng that senario doesn`t happen and we wire before the gas is installed.Sometimes the gas installers set there manifold and meter so close to the meter base that the poco can`t even get their underground in.It always falls back on us since the poco wont set the meter the contractor has us move our meter,sure we get paid to now change a back to back to a split service but it`s a pain and a bother.The NEC has nothing in it about proxcimity to a gas service but does address bonding to it.?????