Will most household ranges operate okay on 208 volts?
Of course they will, they'll just be pulling more currentThe elements will not get as hot at 208V
Of course they will, they'll just be pulling more current
Yes, you're correct. I thought about it after I typed and had a smack myself in the forehead moment.Heating elements are not motors, they're fixed-value resistors. If the R is constant and the V lower, the I and the P will be lower- that's Ohm's law.
Of course they will, they'll just be pulling more current
Sent from my BLU LIFE ONE X using Tapatalk
Looks like everyone beat me to it....![]()
Aren't you at the Institute today?Looks like everyone beat me to it....![]()
I thought about it after I typed and had a smack myself in the forehead moment.
Aren't you at the Institute today?
Roger
They will not get as hot (equilibrium temperature) when energized continuously.The elements will not get as hot at 208V
They will not get as hot (equilibrium temperature) when energized continuously.
But they may be able to get pots just as hot for cooking purposes, just taking longer to reach working temperature.
Waiting for water to boil will be longer!
Waiting for the oven to preheat will be longer.
Once setpoint is reached, probably OK, as seen in thousands of thousands of situations in high rise buildings running 208 Y.
In most cases users will not even be able to tell the difference.
Ha, tell that to the ladies (and male cooks) in the kitchen.
At the parochial school my kids went to a person donated 2 ranges for the kitchen, school had 120/208 3 phase service.
The cooks complained so vigorously that I installed 2 ea 10 kVA autotransformers for them! That 25% power loss is very noticeable on a resistive stove.
Some induction cooktops will provide full heating capability for either voltage if the supply circuits can handle the increased amperage.