Electric range 208 volts

Status
Not open for further replies.
Yes. Most ranges have 120/208 listed on their tag as a secondary value. In most cases users will not even be able to tell the difference.
 
Aren't most ranges rated 208-230v. I'd say look at the data plate. Figure your amperage from the kw for 208v.

Sent from my BLU LIFE ONE X using Tapatalk
 
A range listed to operate at 240 volts will have an rated output approximately of 75% at 208 volts.
 
Heating elements are not motors, they're fixed-value resistors. If the R is constant and the V lower, the I and the P will be lower- that's Ohm's law.
Yes, you're correct. I thought about it after I typed and had a smack myself in the forehead moment.
 
Of course they will, they'll just be pulling more current

Sent from my BLU LIFE ONE X using Tapatalk


So let's look at a 8000 watt range at 240V=== 8000/240 = 33.3 amps

Wattage at 208 is roughly 75% or 6000 watts
6000/208 = 29 amps


More accurately
R= 240/33 = 7.3

P= 208*208/7.3 = 5926 watts
 
They will not get as hot (equilibrium temperature) when energized continuously.
But they may be able to get pots just as hot for cooking purposes, just taking longer to reach working temperature.

I would hope so, otherwise the stove would be worthless :D
 
Waiting for water to boil will be longer!

Waiting for the oven to preheat will be longer.

Once setpoint is reached, probably OK, as seen in thousands of thousands of situations in high rise buildings running 208 Y.

And low rise. There are cities where the only thing available is 120/208- 120/240 is rare as hens teeth.
 
In most cases users will not even be able to tell the difference.

Ha, tell that to the ladies (and male cooks) in the kitchen.

At the parochial school my kids went to a person donated 2 ranges for the kitchen, school had 120/208 3 phase service.

The cooks complained so vigorously that I installed 2 ea 10 kVA autotransformers for them! That 25% power loss is very noticeable on a resistive stove.
Some induction cooktops will provide full heating capability for either voltage if the supply circuits can handle the increased amperage.
 
Ha, tell that to the ladies (and male cooks) in the kitchen.

At the parochial school my kids went to a person donated 2 ranges for the kitchen, school had 120/208 3 phase service.

The cooks complained so vigorously that I installed 2 ea 10 kVA autotransformers for them! That 25% power loss is very noticeable on a resistive stove.
Some induction cooktops will provide full heating capability for either voltage if the supply circuits can handle the increased amperage.

If you are a serious cook, go with gas :thumbsup: I do here you though, it certainly is possible. But not enough to worry excessively IMO.
 