Electric Range Branch Circuit
smallfish
Detroit
I'm inspecting a residential service-panel upgrade when I notice #8 awg THHN copper wires terminated on the load side of a 50 amp two-pole breaker. These 3-wire branch circuit conductors in a nonmetallic-sheathed cable supply an electric range.
The breaker is 60/75 degree rated and so I understand by 2008NEC110.14(C)(1)(a) that these conductors are safely protected. But do I need to expose the range plug and range cord to see if these are also sized for 50 amps for their protection?
Thanks
Thanks
Is the cable SE or NM/Romex?
Since this is a panel upgrade, I imagine the original work is pre 2008 code.
Looks like he has Romex.If the
The breaker should be 40 amps.
334.80 Ampacity. The ampacity of Types NM, NMC, and
NMS cable shall be determined in accordance with 310.15.
The allowable ampacity shall not exceed that of a 60?C
(140?F) rated conductor. The 90?C (194?F) rating shall be
permitted to be used for ampacity adjustment and correction
calculations, provided the final derated ampacity does not exceed
that of a 60?C (140?F) rated conductor. The ampacity of
Types NM, NMC, and NMS cable installed in cable tray shall
be determined in accordance with 392.80(A).