tsnees
New member
- shoreview, MN, Ramsey
Does the floor outlet for an electric range have to be directly behind the range? If not how close to the range must it be?
The instructions for my range included clear and specific dimensions for where the services could be installed (i.e., between X and Y inches from the wall, between M and N inches off the floor, between A and B inches left or right of the center.
422.33 Disconnection of Cord-and-Plug-Connected Ap-
pliances.
(A) Separable Connector or an Attachment Plug and
Receptacle. For cord-and-plug-connected appliances, an
accessible separable connector or an accessible plug and
receptacle shall be permitted to serve as the disconnecting
means. Where the separable connector or plug and recep-
tacle are not accessible, cord-and-plug-connected appli-
ances shall be provided with disconnecting means in accor-
dance with 422.31.
(B) Connection at the Rear Base of a Range. For cord-
and-plug-connected household electric ranges, an attachment
plug and receptacle connection at the rear base of a range, if it
is accessible from the front by removal of a drawer, shall be
considered as meeting the intent of 422.33(A).
You need to comply with 422.33(B).
I think that only applies if you are using the cord as the disconnect (the most common method in my experience)
But I think a breaker lock at the panel would get you out of. 422.33(B)